On Sunday 19 April 2009 21:34, Bruce Dawson wrote:
> I need a continuous mode UPS that will be used 24x365 and it needs to
> supply at least 500 watts for 15 minutes. Note: This needs to be
> *continuous mode*; line-interactive and standby will *not* work (we
> have too many phase changes here). The usual contenders such as APC,
> TrippLite, ... don't seem to have continuous mode UPSes.
Be sure you get a unit that allows hot-swapping the battery.
Unfortunately, the time that you find out the battery is going to fail
in 60 seconds is while the UPS is running during an outage. (Battery
charge-state instrumentation is not terribly reliable.)
You may find this super-conservative approach useful, but you will
need to make an EE-type investigation before buying.
I had trouble with short power interruptions here due to an arcing
feeder line (denied by PSNH for months). The non-continuous UPS would
delay 8 or 16ms before coming on, which would cause most of the
attached equipment to power-reset.
The non-continuous UPS I had, an APC 1100 (1100VA), was a high-end
model that puts out a stepped voltage approximation of a sine wave
rather than a square wave of equal rms voltage (which is OK for running
lamps, stoves, motors.)
I bought a Trip-Lite SU1000RT2 (1000VA, 800W) which is the
"continuous" type you refer to. It solved the line-arc-reset problem
nicely. But rather than discard the APC, I have them hooked in tandem,
the less capable APC feeding the Trip-Lite.
I have been using the series combo for about 6 years now - long
enough to have battery failure in both units. The failed unit beeps
etc, but cannot interrupt power to the equipment. The Trip-Lite
batteries can be hot-swapped. The APC can be turned off for battery
removal. Independent electronics and batteries may offer more
protection than an extra battery for one unit.
Both units have a serial port computer warning/status output that is
supposedly Linux compatible, but I never had the time or need to hook
it up.
>
>... If it
> can use my batteries (deep-discharge marine type), ...
> I've tried building my own with inverters and chargers, but have had
> problems with the batteries dying prematurely (min: 3 months, max: 9
> months).
"Deep discharge" is the problem. The chemistry and plate design for
high-current, rapid discharge batteries leads to an irreversible lead
sulphide build-up on the plates if they are only partially discharged
and recharged several cycles. Also, some of them don't like continuous
trickle charge. (This is from vague memories, so double-check before
accepting it as accurate.)
Jim Kuzdrall